Thursday, April 25, 2024

InspectApedia replies to concerned Missouri mobile home occupant following electrical failure


I'm sorry but not surprised at the electrical safety - or perhaps we should say - unsafe electrical service - that you report. 

Remember that your first priority is to be safe yourself, and then second, to do what you can to let your neighbors or others affected know about safety hazards that you've encountered. Let's hope that the situation you describe doesn't lead to a catastrophic electrical fire, injuries, or  worse. Finally, what you can do is let  your responsible authorities know in calm, clear, well-documented writing, with photos and details - so that the hazards that need attention are on record.

Considering your report that local building officials and the property owner where your mobile home is located in Missouri have not responded to your concerns, that  you have clear physical evidence of an electrical failure that could have resulted in a disaster, you might now want to provide your documentation and case history to the Missouri Public Service Commission - see this web page:

Missouri Public Service Commission complaint website:  https://psc.mo.gov/General/Submit_A_Complaint 

File Your Informal Complaint In Writing                          Speak With A Consumer Services Specialist

Missouri Public Service Commission                                           Call: 1-800-392-4211  
Governor Office Building                                                             TTY: 1-866-735-2460
Attn: Consumer Services Unit                                                      Relay Missouri users may also dial "711" and ask
200 Madison Street, P.O. Box 360                                               the communications assistant to dial 1-800-392-4211.
                  Jefferson City, MO 65102-0360
                  Fax: 573-526-1500                                                                      
                  E-Mail: pscinfo@psc.mo.gov
                  File A Complaint Online  https://efis.psc.mo.gov/Inquiry/Add

Missouri mobile home occupant update on unsafe aluminum electrical wiring in mobile home24

24 April, 2024 AK wrote to InspectApedia by private email:

 I am reaching out to you once more as I'm nearing my court.date trial for eviction court. I have learned that i unfortunately live in a unregulated mostly privately owned monopoly of a city. 

There are nearly no organizations that regulate or enforce rules here and if you believe you found the "one" it most definitely will not be in their jurisdiction. 
 Sadly this city could really use an investigative journalist to make much needed changes. I can not get them to hire an electrician to pull a permit and do the inspection/meter swap. It is imperative,  I need it and I know that I will likely be forced out by them condemning  the trailer at this point but that is what it is going to take to prove my statements in court I suppose. 

This is not a tenant friendly city and attorneys are mentally punishing. I have been told when do you just let go, and by an attorney I respected to leave and stop gripping about it.  I inquired and nearly hired an electrician that sung a different tune when he arrived only to realize I had saw his work vans servicing the area so he likely is contracted for the community. 

It has discouraged me and I am uncertain of the best course of action to have a fair inspection that is not done by someone potentially in the pocket of the investors that own the park. I am sure that sounds ridiculous and I hesitate saying that but it is truly possible.  

Could you tell me by chance of the chain of command when it comes to inspection and regulations for my issues. I have tried Missouri public commission twice now with no luck of jurisdiction.  

I'm going to reach the attorney state general and in a desperate attempt try to wrap this up by the least confusing way I can for a judge. 

Do you have any suggestions or knowledge on how I can find a regulations authority on the matter that can enforce beyond the city? You likely have the most valuable credibility and diagnosis I have been given overall. It is unfortunate that i am still reaching you in regards to the matter,  I apologize for potentially being inconsiderate and a nuisance.  

I am grateful for having found your information.  I imagine you don't stay in one place to terribly long so I wish you safe travels and look forward to hearing from you if availability presents itself sometime soon. Thank you once again for help. 

Tuesday, January 30, 2024

Circuit Breaker Burn-Up Leads to Finding Dangerous Aluminum Wire in Mobile Home

January 2024: Reader Reports Main Circuit Breaker Burn-up at Mobile Home

Reader AK wrote: 

This is from the electric pedestal outside of my mobile home.  It happened June 2nd after my husband and I had been experiencing extremely high Utility bills and redundant replacement of outlets porch lighting but resulting in loss of power to one side of the mobile home ultimately. 

As homeowners we attempted to solve the issue assuming it being a 1970 mobile home we were likely the cause snd at fault for an old electrical system. 

After losing power everywhere but one room we had contacted the utility company to find it was the main breaker that had burned. Since then the  property manager had a random employee of a contracting companies do a simple swap with no inspection. 

Bills continued to rise, and the smell of burnt plastic or rubber was starting to happen at random times. How can I get an inspection or a professional recommendation on what the cause may have been for this? I do have court coming.

... Anyhow, I hope these photos are helpful to you regardless it would just be nice to find a place that could recommend the proper process for these events and maybe a nation wide regulator. 

Publisher (DF) Replied:

I'm traveling between countries so my initial reply has to be a bit brief. I'll look at this further and perhaps I can make some more details suggestions.

Basically it's extremely dangerous to have someone untrained and proper electrical work or electrical inspection examining and pretending to fix electrical services in the circumstances that you described. The risk is of course of a serious building fire with the losses but could then occur.

The actual underlying cause of the burn up of the main breaker could be aluminum wiring, or other improper wiring or improper installation. That's perhaps the most critical circuit breaker in the system since it's the one that provides all of the power to your home.

It would be helpful to know the brand of electrical panel that's installed because some brands are known problems.

And it will be helpful to know whether you're building or service entrance includes aluminum wiring.

Trained license and experience electrician should be able to inspect this installation and give you a reasonable opinion of the underlying cause as models of what repairs are necessary.

But your message certainly suggests that simply swapping breakers when the breakers are burning up is an extremely dangerous thing to do and not only puts property and lives at risk but, as you might suggest that the property manager puts them at risk for assuming liability in such a case.

Reader AK Follow-up: 

This is all I can see, I don't have any information of the age or installation date. They won't likely allow me to have it anyhow. I own a 1970 trailer and have an idea of the wiring inside of the trailer but they have been less then descriptive on any information.

I was told by an electrician that diagnosed the breaker needing to be replaced by the landlord that flickering lights and bad outlets being replaced time and time again were common with the bad breaker. 

Also the high utilities were likely from the arching to the power box and you can actually see the burn hole on the front of the meter where the breaker switches are located on the outdoor panel. Forgive me, I am trying to educate myself on terminology to prevent confusin you and myself. 

I was curious, he has these old meter don't have enough power for all the appliances. I thought the meter was a 200 amp service but there is only one sticker indicating that where the main breaker is. The side that burned out had no sticker on it and we were told it was 100 amp. 

I was thinking maybe we were drawing to much power from all of the appliances and electronics opposed to the previous tenant who was an elderly woman who lived alone with a TV a fridge and a couple of air units. I don't have nearly enough education to dispute anything. 

I just am trying to inform you best I can from what a electric technician a maintenance man and a journeyman electrician have stated about the high bill the arching the bad outlets and wiring and amperage. I have no idea what happened beyond this but I will try to gather any information I can. I do believe they have processes that they are legally supposed to follow for this kind of thing.

Moderator (Daniel) Replied:

I'm still traveling between countries so my replies are but partial. 

Watch out: But for a 1970s trailer it's really important that you find out whether aluminum electrical wiring was used for the branch circuits. If so and if it hasn't been repaired, that's a serious fire hazard. 

Flickering lights and intermittent electrical failures can be a sign of that problem.

It's easy to determine. Just have your electrician look inside the electrical panel that contains the branch circuits for your home.

Reader AK Confirms: Aluminum Branch Circuit Wiring Found

I wanted to tell you thank you once more for taking time out of your day to respond. When I initially sent the photos and message, I wasn't really expecting much so when you responded I took the time to look at your bio and resume and I was honestly shocked at the credentials you have and thought wow, no way. I can't believe he actually responded.   My husband was intrigued and I have to admit much more savy in the construction world then myself. This is all foreign to me,  I have had no business tinkering with most trades especially electrical.

I try , I try I do what I can if possible.  He told me it is aluminum wiring that branches and I said I would mention it to you and that you had been traveling but I think it best if there are any other questions and for accuracy sake he take over. We are both very appreciative you responded especially with a busy schedule. It helps to have someone with proven credibility to give advice narrowing it down. At your earliest convenience and if you have an opportunity feel free to reach us anytime if  you can.  

We currently have gotten in a position to prove management neglected to send work orders or an electrician but the utility company has gone as far as to avoid me until I hounded long enough mentioned court dates coming, then continue to give me the run around about the name being under the wrong email and account and sent 8 other individuals an email to proceed to send the mayor an email. 

They knew what happened and closed my account with in 30 days permanently with no notice sticking firm to finalized for non payment. Now since it has been 90 days it can't be turned back on without an inspection but when it caught fire nobody wanted to look at it. Aside from already damaged wiring and smells of burnt plastic or rubber when it is actively powering the house we just couldn't afford the bill any longer and had no resolve at that point in time.

Moderator (Daniel) Replied: what to do if your home has solid conductor aluminum electrical circuits

Bottom line: solid conductor aluminum wire branch circuits are a very serious fire hazard, repairable by pigtailing short lengths of copper wire to the aluminum wire using special connectors.
But watch out: the fire hazard might even be increased if improper repairs are made or if repair attempts are made using the wrong connector. 

So to repair your home properly, from the electrical panel onwards throughout the home will require an electrician who is familiar with aluminum wire hazards AND with the only correct repairs. So you can tell, even as an amateur, if the electrician is NOT the right person if she or he wants to use "wire nuts" - a twist-on connector, to do the copper pigtailing. 

The more you can stand to read about this topic the better you can judge if your repair electrician is the right person for the job. 

See at the very least:

This page that summarizes the repair options, of which the current most-used is method #3 on this page, the AlumiConn 


To understand the issue, see Dr. Aronstein's article at https://inspectapedia.com/aluminum/Aluminum_Wire_Hazard_Reduce_2011.pdf

Or this web page version of that information: https://inspectapedia.com/aluminum/Aluminum_Wiring_Risk_Reduction.php

And if anyone tells you that your aluminum wired circuits, if they have not been "repaired" as described above are "safe" they're wrong - as we explain at


You are welcome to give all of these documents to your electrician. My advice is DO NOT permit any other repair methods - as they're not safe. 

If there are other older mobile homes or trailers where your home is located, particularly homes built in the 1970s, you'd be doing your neighbors a very good service to advise them to have tiehri wiring checked too. Mobile home fires are among the most dangerous. 

IF FIRE OCCURS (from any cause) - homes with Aluminum Electrical Wiring or in Any Home

KNOW WHAT TO DO IF FIRE OCCURS. HAVE A PLAN. DISCUSS IT WITH THE WHOLE FAMILY. SEE YOUR LOCAL FIRE DEPARTMENT FOR GUIDANCE.

INSTALL SMOKE and CO DETECTORS in your home. EARLY WARNING IS VERY IMPORTANT.




InspectApedia Editor at Work


We're thrilled to announce that as of 1 June 2021 Amy Church has signed on as editor in chief of InspectApedia.com.  We call her "eagle eye" as she combines a broad view of InspectApedia article content clarity and content with a sharp eye for mis-placed hyphens. Amy joins publisher Daniel Friedman in making sure that we balance our time researching and writing articles for our website with responding to requests from our readers. 

InspectApedia exists for our readers. Thank you for 18 years of reader questions and suggestions and content contributions. 

Daniel

Thursday, August 30, 2018

This is construction adhesive, not harmful mold

Don't get scared by unfamiliar stains or materials you see in or around your building that are not mold.

A number of readers have taken advantage of InspectApedia.com 's feature that allows posting of photos (one per comment, no limit on number of comments) of growths, stains, or substances in or on their home to ask "is this toxic black mold"?

First, of the millions of mold genera/species, there are many that are not black or even dark in color but that can be harmful to humans as an allergen, pathogen or toxin. So the focus on "black mold" can get us in trouble.

Second, knowing the genera or species of mold won't change what needs to be done about it one bit.
- Remove the mold
- Remove moldy materials that can't be cleaned, such as moldy drywall or insulation
- Clean the exposed surfaces
- Find and fix the leak that caused the mold

Third, stuff that is not mold does not usually merit a costly clean-up procedure, normal cleaning may be all that's needed.

Finally, some substances that people ask about can simply be left alone, such as this construction adhesive on the under-side of a plywood subfloor that had worried one of our readers.

See MOLD APPEARANCE - STUFF THAT IS NOT MOLD at https://inspectapedia.com/sickhouse/Stains_Not_Mold.php

and
See MOLD APPEARANCE on VARIOUS SURFACES - INDEX  the full list of photographs of the appearance of mold on various building materials & contents.
found at https://inspectapedia.com/mold/Mold-on-Building-Surfaces.php 


Monday, March 06, 2017

InspectApedia mobile update

2017/03/06 Thanks to Clark Van Oyen, Countable Web Productions - Cloud services design consultant for InspectApedia.com and to the public for providing css and other updates that allowed InspectApedia.com to change to a responsive website design. Viewers on desktop, laptop, tablets, and smartphones all now see the same InspectApedia.com content, but formatted for easiest viewing on their device. 

We continue to add new and expanded technical content to InspectApedia.com daily. The website currently offers more than 10,000 articles, illustrations, and technical documents providing researched information about building & environmental inspection, testing, diagnosis, repair, & problem prevention advice  

Saturday, June 18, 2016

New Feature at InspectApedia.com  OLD HOUSE MYSTERIES & SOLUTIONS

We post photographs & descriptions of unidentified objects, components, systems, materials in buildings, inviting reader comments to help us track down the history or origin and use of unfamiliar  things we find in, on, or around buildings. 

Photo of perforated roof sheathing boards with ceramic inslators

What do you suppose is the origin or was the purpose of these roof sheathing boards perforated at regular intervals and mostly equipped with ceramic bushings. 

Contributed by home inspector David Grudzinski we illustrate and discuss these boards at 

Friday, May 17, 2013

InspectApedia.com goes Mobile

After struggling for 3 years to find a way to take InspectApedia's thousands of articles into a clean mobile website format, with helpful advice from my Google AdSense team I've found a remarkable automated solution using dudamobile.com. dudamobile uses a masking approach to provide mobile-formatted translations of classic html pages and websistes.

The new mobile pages can be edited globally or individually using tools provided by dudamobile, but key is duda's ability to provide a usable and automated conversion of an existing website.

In just 24 hours my mobile site was running and in less than 48 hours it was clean enough for public display.

If other publishers need help with such a project just ask and I'll be glad to review what I did. Key was figuring out how to avoid re-coding the original site or worse, trying to create two versions of the site, one classic-desktop and a second in mobile form.

See InspectApedia Mobile at http://m.inspectapedia.com/

to see how InspectApedia now looks on your mobile phone. Of course we will continue to maintain the classic - desktop version of InspectApedia.com as well. Changes and additions to InspectAPedia will appear automatically on our mobile site thanks to the AdSense team's advice & dudamobile.com 's stunning support. Special thanks to Google's Richard Scialabba and dudamobile.com 's Russel Jeffery who made this remakable transition possible, fast, and inexpensive.
 
Daniel Friedman
Editor/Publisher - InspectApedia.com

Thursday, February 12, 2009

US Economical Problems, Weather, Oil Costs Lead to Increase in Mold & Water Damage in Buildings

September 2010: Recent Flooding & Water Damage in the U.S.
Photograph of a moldy flooded basement.
Building water damage and mold remediation companies are reporting record levels of homes damaged by water, burst pipes, ice dam leaks, and fires as homeowners try to cope with high heating costs, unemployment, and cold weather.

The principal causes of this surge in fire and water damage in private homes during the winter of 2008-2009, but continuing due to extreme weather conditions during the spring, summer, and fall of 2010 in the U.S. are probably a perfect storm of financial troubles, increased heating costs, home foreclosures, and winter weather that included ice storms and severe cold snaps.



Our site offers impartial, unbiased advice without conflicts of interest.
We will block advertisements which we discover or readers inform us are associated with bad business practices,
false-advertising, or junk science. Our contact info is at


InspectAPedia.comInspectAPedia.com





High Prices for Home Heating Oil during 2008 and early 2009 Led to Increased Home Leaks


A one-two-three punch of the Great Recession, skyrocketing unemployment, and galloping home heating costs has led many homeowners across the U.S. to turn down the heat in their house.

But in many homes the result of that savings on heating cost has led to an enormous cost to clean up water damage and mold resulting from frozen and burst water piping.

A combination of setting the thermostat lower than ever before, a pipe passing through a cold or drafty building corner, and perhaps homes being empty or even running out of heating oil leads to catastrophe for some homeowners.

In the articles listed below we provide detailed free advice to help building owners avoid these problems.


Unsafe Chimneys, Wood Stoves & Auxiliary Heaters Cause More Fires during 2008-2009
Photograph of a damaged masonry chimney.
High home heating costs combined with unemployment or reduced income for many families also led to an increase in the use of auxiliary heaters, kerosene heaters, wood stoves, coal stoves, and other heating appliances. Our file photo shows a home badly damaged by a creosote fire in a metal chimney that had been venting a wood burning stove.

Improper installation, inadequate clearances between the heater and combustibles, and failure to inspect and clean chimneys has led to an increase in house fires during the winter of 2008-2009.

CHIMNEY INSPECTION DIAGNOSIS REPAIR - advice on inspecting and repairing chimneys.

Wood Burning Heaters Fireplaces Stoves -important safety advice for these appliances.

Ice Dam Leaks in Buildings Add to Winter Water & Mold Damage

Ice dams on a slate roof (C) Daniel Friedman
In addition to the heating and winterizing SNAFU's cited above as sources of increased leaks and mold damage to homes during the winter of 2008 and 2009, a combination of very cold periods of winter weather and inadequate attic ventilation led to formation of ice at building roof edges.

Melting snow backs up over the warmer roof surface areas and leaks into the building causing ice dam leaks.

See Ice Dams & Attic Condensation & Prevent Ice Dam Leaks in Buildings for an explanation of what causes ice dams and leaks and how they can be prevented.

Empty Homes Especially at Risk of Leaks, Water Damage, & Mold Damage

Flooded home, Jasper TX (C) Daniel Friedman
The combination of the Great Recession economic collapse, high unemployment, and bank foreclosures has left many homes standing empty during the winter of 2008-2009.

Many empty homes were improperly winterized or were not winterized at all, while at others the fact that the home was unattended meant that the heating system could fail without anyone taking notice.

The result was a higher than usual number of homes suffering leaks and water damage from frozen, then burst water piping.

At the top of this article we listed resources at
InspectAPedia.com® that can help homeowners, banks, and other property owners avoid further costly damage to their properties.

InspectAPedia.com is an independent publisher of building, environmental, and forensic inspection, diagnosis, and repair information for the public - we have no business nor financial connection with any manufacturer or service provider discussed at our website.

We are dedicated to making our information as accurate,
complete, useful, and unbiased as possible: we very much welcome critique, questions, or content suggestions for our web articles. Contributors, even if it's just a small correction, are cited, quoted, and linked-to from the appropriate additional web pages and articles - which benefits us both. Working together and exchanging information makes us better informed than any individual can be working alone.

A brief summary about InspectAPedia.com can be read atstyle="font-family: Arial;"> http://inspectapedia.com/About_Us.htm



-- Daniel Friedman

This Blog is about Home & Building Problems & Building Environmental Problem Diagnosis & Repair. We provide diagnostic field and forensic laboratory investigation services. In depth information is at
InspectAPedia.com. Website content suggestions are most welcome. Contact Us.

Building Problem & Environmental Problem Case Histories: Here we post summaries of field investigations of all sorts of building & mechanical system problems. We also post environmental and foernsic lab toxic or allergenic mold and other indoor air quality investigations. We omit private information. We describe observations, procedures, and findings helpful to readers who are trying to remedy their own mold, allergenic, carbon monoxide, odor, or other indoor air and related health concerns in their indoor environment.

Sunday, September 03, 2006

Advice for tenant in moldy apartment

What can a tenant do when s/he discoveres that s/he is living in an intolerably moldy apartment?

What follows is an email, slightly edited, from a tenant in a moldy apartment in Kentucky. The risk in her situation is increased because she suffers from a compromised immune system. My advice to her follows her letter.

Tenant describes a moldy apartment
I appreciate the user friendly format and the wealth of information on your website. I'm suffering severely from mold related illness and I need immediate help.

Two months ago I moved into a new apt. Ever since I have had terrible congestion that appears w/in a minute of entering the apt. And only clears up after hours of leaving the apt. I have gone and had allergy testing and find I am highly allergic to *most* molds.

I have found a black shadowing mold like substance on the walls coming from beneath the kitchen cabinets. The *dust* settles on the edge of the counter at the wall beneath the cabinets. The dust is large particles that look a lot like black pepper. It also sticks to wall on the way down.

Possible causes of apartment mold, possible extent of mold

I have been made aware of a leaking roof in the 2nd floor apartments so severe that requires buckets to contain. The water, I have been told runs down the walls into the ground floor apartments where I am a tenant in one. The apartments are known to be old and from the road I can see large blackish streaks across the light brown roofing.

What steps the tenant has already taken

I've just bought two HEPA filters for the bedroom and living room which has seemed to make a significant difference in the severity of the congestion. Also, I have been told that the air conditioning and heat is run on a water coil system (the air is circulated through all of the apartments) which happens to be in my bedroom closet. when I removed the vent to put a filter in I found mold covering the bacck of the metal slats in vent cover. I cleaned it with bleach.

Wants to move

I need to move because I cannot live with this building-related sickness. It is important to know what I'm dealing with before I go to management, because it seems to be such a severe structural issue, they may try to do something underhanded and cover it up.

Compromised autoimmune system increases risk to tenant

Also I have some sort of autoimmune condition(Lupus, MS they haven't pinned it down) I am no longer able to do what I went to school for. My fine motor skills are compromised(and I have slight tremor).

I have a year lease and need to handle the situation in a way that will allow me get out from under this situation w/out my being taken advantage of and I am no expert in these matters.

Please let me know when you have a moment how I can handle this terrible situation(err, the mold) thank you so much for taking the time to read this lengthy missive.


Action Advice for Tenants in Moldy Apartments

I'll help as I can but keeping in mind I'm distant and can't see all of the conditions. Therefore my advice can only be general, and we must keep in mind that there could be important observations that might change the assessment of your situation as well as the advice on steps to take.

What you describe sounds severe and building-related.

Possible hidden mold

The mold that you *see* may not by any means be the whole problem, or even much of the problem; various species could be in building cavities and in the HVAC system. Also, "bleaching mold" is never a successful remedy for a moldy building. The places where mold is growing must be found, moldy material removed, exposed surfaces cleaned, and the causes of mold growth corrected. If the area of mold growth is large (more than 30 sqft) the work needs to proceed with special procedures to avoid spreading moldy dusty debris around.


Compromised immune system increases vulnerability to mold-related illness

The fact that your immune system is compromised places you at extra risk and means that you and the contents of your apartment need to be protected carefully.

Some possible mold reservoirs in the building

You describe two apparent sources, and of course there could be other sources from other leaks or problems you haven't discovered:

Roof - can have leaked into ceilings and walls; depending on what buildng marterials used, they could be moldy with problem molds.

HVAC - If there is a common A/C duct system which has become mold contaminated, no amount of cleaning in your immediate apartment would be sufficient since it is possible that the whole system needs to be cleaned, or possibly some duct sections replaced, and the cause corrected. Also it is common for A/C condensate or water from a chiller system to leak; water could have leaked into your closet ceiling and walls, also creating a problem mold reservoir.

Very often when I visit a site I find other leaks and mold sources that need to be addressed, so I wouldn't assume these are the full extent of what needs attention.

Building management reluctance to address mold problems properly

Sometimes a buildng management is reluctant to face the expense and trouble of handling this situation correctly - which would involve a thorough building survey, evaluation, diagnosis of problem areas and their causes and specification of the steps to remedy them, followed by performing of the work followed by clearance inspection and testing by someone not at all connected with the contractors performing the remediation.

Reluctance of building managers to address mold also comes from the wish to avoid alarming other tenants. In my experience this is always a mistaken notion, as tenants talk to one another anyway, and building-related illness frightens people - fear spreading faster than mold growth. Accurate information and the assurance that tenant concerns are being handled competently is more effective than other less direct responses by building management.

Half-baked or amateur workmanship risks increasing the ultimate cost to the building management by making building occupants sick and contaminating their belongings.

What a tenant can do about a moldy apartment

1. You should notify building management in writing of unhealthy unsafe conditions that need attention and that you are unable to live in the apartment.

2. You might be successful in identifying some of the mold suspect material you see as problematic, and you might collect a settled dust sample to see you can pick up indications of other problem molds or allergens. However identifing mold in an apartment, while it may convince building management to act, does not and cannot establish the level of exposure that an individual has had to the mold found, nor does it assure that the mold identified is the only or even the main hazard. The prime use of tenant sampling in this case is to show management that there is at leastsome evidence of problem mold in the building

Our mold sampling instruction contains sampling instructions you can follow. I'm on assignment out of the U.S. and won't be processing any lab samples until after 9/10 so if you are in a rush you should use another lab but you can still follow my sampling procedures.

3. If building management elects to make some effort to deal with the problem:

3.a. be sure that the work does not create demolition debris and mess which contaminates or further contaminates your belongings, especially soft goods like curtains, carpets, bedcovers, which may then require cleaning, and worse, upholstered furniture which might not be able to be cleaned adequately.

3.b. if your posessions are already likely to be contaminated with moldy dust they should be cleaned before taking them to a new home; soft goods can be laundered or drycleaned; hard surfaces can simply be washed or wiped. Moldy upholstered furniture is in question depending on how bad it is; surface dust can be vacuumed off of it; if upholstered furniture has been wet or has had mold growing on or in it it is probably not salvageable without complete reupholstering from the frame up.

The more you know about proper procedures to find and clean up moldy buildings the better you can assure that your situation is handled properly. The articles at these links might be helpful:

The Mold Action Guide

When to Hire a Mold Professional

FAQs about Mold

Keep me posted on how you proceed.
Best wishes.

Daniel


This Blog is about "What to do about mold in buildings"
When is mold a problem in buildings? What should be done about it? Find expert field and lab testing, inspection, remediation advice, but ... avoid "fear of mold" and bogus advice which can both cost you and yet may not really address the problem effectively. My interest is in providing expert service to my clients, protecting not only their health but their wallets. I provide field investigations to find problems and to recommend solutions to mold in buildings, and I operate a forensic laboratory in New York which accepts mold and other indoor air and particle samples for examination. In depth information is at www.inspect-ny.com and the links at that page. Website content suggestions are most welcome.

Case Histories: Here I post summaries of field and lab toxic or allergenic mold and other indoor air quality investigations. I omit private information. I describe observations, procedures, and findings helpful to readers who are trying to remedy their own mold, allergenic, carbon monoxide, odor, or other indoor air and related health concerns in their indoor environment.

Sunday, April 30, 2006

Will "Black Mold" Return if Moisture is Kept Low?

Black Mold Question from a Reader:



I have been finding your site very informative, and have a question (actually a statement) but can you confirm if the following is mainly correct?

Black Mold is found everywhere, in nature, outdoors, indoors etc. It isnt until a constant moisture source and humidity conditions are present that the black mold might actually become a problem, forming in colonys, creating problems, toxins etc. And once those conditions are take care of, with due care to avoid cross contamination, and moisture problems are taken care of and humidity levels are under control, the mold can be properly remediated and therefor resolved as long as moisture problems are constantly checked on for further invasion and damage, and things that are installed (ie: C/A etc) to help humidity issues are cleaned properly.

Thank you,
N.R.

"Black mold" is not the issue



Reply from D.F.

Black mold is not necessarily the issue in a building. Public fear that is focused only on "toxic black mold" is a bit of confusion caused by media attention to the Stachybotrys chartarum scare.

1. Some black molds are perfectly harmless such as black mold found on much new framing lumber and which is in the Ceratocystis/Ophistoma group - a cosmetic only mold which is not harmful to humans and which
does not rot the wood.

2. Black mold, even if a toxic one may not be what is making occupants ill: Some black molds that people fear, such as Stachybotrys chartarum, are not normally airborne and become so only in response to violent disturbance such as during demolition. So even though this mold can be toxic and seems to be associated with a wide range of complaints, the fact that it is seen on a building wall does not assure that this is the mold to which building occupants are being exposed.

3. Visible mold as a moisture indicator: Black mold" in a building thus should be considered an "indicator" mold of wet conditions, and a careful inspection is in order. While S. chartarum is a "black mold" which can be harmful, almost always, when this mold is found in a building, or when other "black molds" are observed (some are not relally black but look so on a surface and outside the microscope), I find other more problematic but harder to see but more airborne molds such as Aspergillus sp. when I inspect thoroughly.

What is important, particularly if people are sick, is to have a building expert, someone who knows where and how to look for problem molds in buildngs, inspect the property to find the leak history, mold reservoirs, and to do enough mold identification to assure that the real problems, if any, have been found and that the scope of cleanup work can be specified.

I emphasize point #3 because in most of the buildings I inspect, where an occupant has become worried about "black mold" someone has seen, the dominant problem molds in the buildings are NOT the "black molds" that were observed but rather harder to see light colored but more-airborne smaller spore and often toxic or pathogenic molds such as those in the Aspergillus sp. group.

I agree that once a building has been established as adequately clean of mold, monitoring leaks and humidity are key.

I agree that if we keep indoor humidity at proper levels and do not permit leaks and moisture problems to go unattended, we would not expect problematic indoor mold growth.

More in-depth discussion of these points can be read at the following articles:

Mold Action Guide - my main "Mold Action Guide" step by step instructions on what to do about mold in buildings

How to Look for Mold

How to prevent mold list of articles

How to Prevent Mold in Buildings main article on this topic

How to Get to Mold-Resistant Level of Indoor Humidity

Responding to Building Leaks and Floods to prevent rapid problem mold growth in buildings.

If you or other blog readers have other content suggestions I'd appreciate hearing from you.

Daniel Friedman
dfriedman@inspect-ny.com
www.inspect-ny.com

This Blog is about "What to do about mold in buildings"
When is mold a problem in buildings? What should be done about it? Find expert field and lab testing, inspection, remediation advice, but ... avoid "fear of mold" and bogus advice which can both cost you and yet may not really address the problem effectively. My interest is in providing expert service to my clients, protecting not only their health but their wallets. I provide field investigations to find problems and to recommend solutions to mold in buildings, and I operate a forensic laboratory in New York which accepts mold and other indoor air and particle samples for examination. In depth information is at www.inspect-ny.com and the links at that page. Website content suggestions are most welcome.

Case Histories: Here I post summaries of field and lab toxic or allergenic mold and other indoor air quality investigations. I omit private information. I describe observations, procedures, and findings helpful to readers who are trying to remedy their own mold, allergenic, carbon monoxide, odor, or other indoor air and related health concerns in their indoor environment.

Monday, March 06, 2006

Mystery blobs - is it mold? is it Mildew? What Mold Tests do I Order?

This Blog is about "What to do about mold in buildings"
When is mold a problem in buildings? What should be done about it? Find expert field and lab testing, inspection, remediation advice, but ... avoid "fear of mold" and bogus advice which can both cost you and yet may not really address the problem effectively. My interest is in providing expert service to my clients, protecting not only their health but their wallets. I provide field investigations to find problems and to recommend solutions to mold in buildings, and I operate a forensic laboratory in New York which accepts mold and other indoor air and particle samples for examination. In depth information is at www.inspect-ny.com and the links at that page. Website content suggestions are most welcome.

Case Histories: Here I post summaries of field and lab toxic or allergenic mold and other indoor air quality investigations. I omit private information. I describe observations, procedures, and findings helpful to readers who are trying to remedy their own mold, allergenic, carbon monoxide, odor, or other indoor air and related health concerns in their indoor environment.

Client asks about indoor mildew, strange wall blisters, and what mold to test for



Email questions:

First off thanks for your very detailed website. I have a question about what to sample for a mold analysis. We are renting a home a home where there is what appears to be visible mold on some of the interior surfaces of exterior walls. I have shown this to the management here; however, they repeatedly minimize/ignore the problem and will not do any testing.

We have explained that my partner has been having health/respiratory problems that we believe might be connected to mold, so we would like to have this identified in order to take care of our health. In turn they simply doused the area with bleach. That was a week ago and it has already started to grow back.

In the meantime, they have claimed that this was simply "surface mildew" and their lawyers have written us a letter to warn us, well, I'm not really sure what it is to warn us, but mostly it seems like an attempt at intimidating us even though they admit it is a common problem in this community. It does however seem like it could be primarily a surface problem as all the walls are bizarely impenetrable--old military housing.

Since it is a rental unit (therefore we can't do bulk sampling) and the mold is visible, we are wanting to do simple tape-lift sampling for identification purposes. Until we get some handle on what we are dealing with we can't really decide how to proceed.

The question that I have for you pertains to an unknown substance. Once we performed the first cleaning of this substance in our closet, which was heavily effected, the substance began appearing in other rooms where it had not been before (the same after they doused it with bleach). After it had spread, I found what appeared to be a simple bump in the paint on one wall. I rubbed a washcloth across it, and the bump was actually a white surfaced, kind of creamy yellow goo (not a scientific term, I apologize)--the best description that I have for it is that it seemed kind of like brie with the white outside and the inside was similar, kind of yellow, soft, etc. Underneath that was the paint. After they did their bleaching, more bumps appeared in the paint in other areas of the house, as though there were something liquid under them. (They are soft and squishy.) As I said I am no expert in mold, therefore I am not sure if this sounds like it could be connected to you. Does it sound like something that we should tested, and if so what is the best way to get that done/get it to you?

Thank you very much for your time and any insight that you can provide -- Dianna, 3/1/2006

Our Response - Sounds like water and bleach behind paint - excessive and improper "surface cleaning" does not correct a problem mold reservoir



1. There is no mildew in buildings. Mildew is an obligate parasite that grows ONLY on living plants - so unless your home is made of grapes or lilac leaves there is no mildew on it. What grows in buildings that looks like mold is mold. Some mold is harmless-cosmetic; some is allergenic; some can be pathogenic or toxic. People who are at extra risk such as with immune disorders or respiratory concerns are at extra risk.

Tips on how to look for mold are at
http://www.inspect-ny.com/sickhouse/lookmold.htm

Tips on how to use your flashlight to spot hard-to-see mold are at
http://www.inspect-ny.com/sickhouse/mold.htm#lightuse

Pictures of what mold looks like in a building are at
http://www.inspect-ny.com/sickhouse/mold.htm

Stuff that is not mold but is sometimes mistaken for it is shown at
http://www.inspect-ny.com/sickhouse/NotMold.htm



2. The mold you see might be "surface" mold or it might be the tip of an iceberg of a larger mold reservoir - the distinction depends on why it's growing where it is and where leaks have been throughout the history of the building. If all you see is a small area (less than 30 sq.ft.) it is unlikely to be the principal problem in a building but it might indicate that there is a larger but un-detected problem. My web articles discuss how to look carefully for mold.

3. Sampling - you can't do invasive inspecting like checking wall cavities but you can
- notice evidence of a history of leaks into building cavities - which raises the level of risk of hidden problems
- notice where there is visible mold and collect a few surface samples using tape www.inspect-ny.com/sickhouse/bulksamp.htm has the procedure - sample things that look different by color, texture, or by what they're growing-on (drywall vs. wood for example).
- collect a sample of settled dust from one representative area, perhaps a bedroom, to see if we can pick up unusual levels of problem mold spores in that material - which would indicate that there has been a high airborne mold level at some time.

Instructions for easy and inexpensive tape lift sampling are at
http://www.inspect-ny.com/sickhouse/bulksamp.htm

4. Bleach - if building maintainers used bleach as a "mold treatment" that suggests that work is being done by people who lack good information about how to clean up or "remove" problematic mold in a building. The object is to remove problem mold, not to "kill it" since "killed spores" even if you could kill them all (which you can't) may still be allergenic or toxic to the occupants. Further, surface treatments ignore possibly significant hidden mold reservoirs.
Finally, any demoltion or "cleaning" that blows dust all over the apartment or your belongings is at risk of increasing rather than reducing the health risk in the building.

5. Wall blisters? From your description of blisters appearing only after someone bleached and washed the wall surfaces (superficial and perhaps inadequate mold cleanup) I don't know what you've observed or even whether or not it's mold - yellow goo? It sound ass if your observations may be leak or moisture related which in turn are key factors in assessing mold risk. If the walls were treated with strong bleach and water it's possible that that substance has damaged, penetrated, and is causing blisters in the paint. I'd try pricking a blister and collecting the liquid for analysis.

I'd inform the "lawyers" that the cost of making you sick or sicker, or the cost of having to do extra cleaning if the apartment people don't follow proper procedures, or the cost of having to inspect and clean the building repeatedly because they're starting off with shortcuts are all likely to ultimately cost the building owners a lot more than the cost of doing it right the first time.

-- Daniel Friedman 3/1/2006

Saturday, January 14, 2006

How Low Should You Keep Indoor Humidity to Avoid a Mold Problem

This Blog is about "What to do about mold in buildings"
When is mold a problem in buildings? What should be done about it? In depth information is at www.inspect-ny.com/welcome.htm#environ and the links at that page. Website content suggestions are most welcome.


Case histories: Here I post summaries of field and lab toxic or allergenic mold and other indoor air quality investigations. I omit private information. I describe observations, procedures, and findings helpful to readers who are trying to remedy their own mold, allergenic, carbon monoxide, odor, or other indoor air and related health concerns in their indoor environment.

What indoor humidity should we maintain in order to avoid a mold problem?



We're going to discuss maintaining an anti-mold low humidity level in a building which does not currently have a mold problem. No dehumidification system will be up to the task of preventing mold if a building has serious leaks, flooding, or water entry. (© Daniel Friedman 2006 All Rights Reserved.)

And no dehumidifier, no "air cleaner," no "ozone generator," nor other magic machine, spray, or air treatment will correct a mold problem in a building if there is a significant problem reservoir. For that case, what's needed is to find the mold problem, remove it, and correct its cause. And as a last warning, there are about 1.5 million mold species - some of them may be able to grow in very dry or very wet or other inhospitable conditions.

We're therefore focused this article on the common indoor problem molds in this article. The genus I refer to include some common problem indoor molds such as Aspergillus sp., Penicillium sp., Stachybotrys sp. /S. chartarum /Memnoniella echinata, Trichoderma sp. /T. viride, Ulocladium sp. /U. chartarum, and at a less significant level of concer, Cladosporium sp. - the king of molds and its competitor Alternaria sp.

Suppose a building does not currently have a mold problem, or a mold cleanup project has been completed.

How low should we maintain interior moisture to avoid a mold problem?



1. be sure there are no ongoing building leaks, water entry, or venting problems.

2. keep the indoor humidity level in the mid-comfort range. A maximum indoor relative humidity of 55 should be ok, 50 better, 45 for an attic knee wall provided there are no ongoing leaks and the attic space is not one which is being vented to outside (in that case you're not in control of the humidity. If you run humidity too low or too high the building occupants will be uncomfortable.

Technical background on indoor relative humidity (RH) control:
this is getting slightly more technical about measuring the relative humidity.

Controlling Humidity in Basements



If the RH in the center of a basement is 55% it is likely that at the walls or corners, where there is less air circulation, the RH may be different. The local temperature difference close to a cool masonry wall surface means that both temperature and measured relative humidity close to the wall will be different than in the center of a room.

But it's at the cooler wall surface that condensation may be expected to occur.
If you measure the RH at the worst-case location such as the most-suspect-of-dampness corner of a basement and you're 55% close to the wall you're likely to be ok.

Controlling Humidity in Attics



In the case of an attic crawl space, perhaps a knee-wall area abutting an upper floor bedroom, the risk of excessive inside humidity at a wall is much less than in a basement. In the attic we don't face a cool concrete-block wall surface in the attic.

But what about an un-vented attic in a cold weather climate? Heat loss into such a space and warm moist air leaking into such a space can indeed create high levels of problme moisture - enough to wet surfaces or even form frost and later drip onto the attic floor.

On the other hand, if the attic is vented to outside (ridge vents and soffit vents as I recommend) you'll never control the attic RH. You'll be trying to control the whole outdoors.

On the third hand (if that's possible), if an attic is not vented to outside, the RH
there is most-likely a function of and approach the levels of the humidity levels in the air in the rooms abutting and below the attic area.

Choosing the target humidity RH level



One client said he could keep the basement at 55 but didn't want to push it below that. Is this enough safety margin?

At 60% indoor RH we're entering the indoor problem mold-formation risk zone of high interior moisture in building wall or ceiling cavities or on wall and floor surfaces, possibly conducive to mold growth.

If you set the RH target at 55%, you're operating with **not much safety margin** of dryness. A small change in outdoor conditions (spilling water by the foundation) or indoor conditions (a nearby roof, wall, window, plumbing leak) can increase the moisture and RH into the problem zone. If for reasons of dehumidification cost you have to operate close to the edge, extra attention to leaks, moisture proofing, roof and surface drainage are even more important.

When have you reached your RH target?



If a building has been damp for some time, moisture has been absorbed into various materials such as wood framing and masonry surfaces. It may take weeks or even longer to drop the humidity in such an area, as the moist materials also have to dry out, not just the air. Using a fan to increase air movement in the area being dehumidified can speed this process.

Warning: if you cannot get the indoor RH down to a low level in a below-grade area such as a basement or crawl space, I'd suspect that too much moisture is continuing to enter through the slab or masonry walls. Attention to outside drainage may not be enough. In such cases, coating the walls with a masonry sealer (Thoro-Seal(TM) or Dry-Lok(TM) are example products) might help.

If you want to get past this practical discussion of indoor humidity and mold, check out "Understanding Ventilation," by John Bower. The Healthy House Institute, 1995.

More than a normal person can stand to read about what to do about mold in buildings is at my website. You might start at the "Mold Information Center - What to Do About
Mold in Buildings"

Hope this helps.

Daniel Friedman dfriedman@inspect-ny.com www.inspect-ny.com/welcome.htm#more

Sunday, November 06, 2005

Some Black Mold is a Harmless Stain That Came With Your Framing Lumber

Don't mistake this harmless black mold for "toxic mold contamination" on wood framing in your building. It's a cinch to determine that it was there at the time of construction. It's probably Ceratocystis/Ophistoma.

One of my clients in the Northeast saw "black mold" on floor joists overhead in his basement ceiling. He launched a $600,000. cleanup campaign with his insurance company, lawyers, investigators, the works.

In this case, even a cursory inspection by an investigator who was familiar with this particular mold could have disclosed that the "black mold" that frightened the owner was of really no concern other than as a cosmetic issue.

Cosmetic-only mold, or "bluestain" is often found on framing lumber. Two famlies, Ceratocystis sp. and Ophistoma sp. produce black surface molds on lumber that has been left wet, usually from being stored outdoors. (So much for "kiln dried" lumber your builder paid extra for.) There are [with only obscure exceptions] no health hazards reported from exposure to these molds, and they are not wood rotters. This is a cosmetic problem.

Few experts would be so bold as to assert that they could identify a surface mold without microscopic examination. This group is a reasonable exception.

See the black mold on this wood beam? It's only on one of three 2x12s. This mold was on this 2x12 at the time of construction, it's not growing in the house.

Look at the sudden stop that the "black mold" makes on this plwyood roof sheathing where the (black moldy) edge of this rafter meets the roof sheathing !

Sure the attractiveness of a growth surface to individual mold species varies by what that surface is made-of, and a rafter is not chemically identical to the plywood roof sheathing. But they're both cellulose. Mold growing on a wood structure would not be expected to make such a sudden stop at the plywood if it had in fact been actively growing in this location after the house was built.

For another clear phenomenon of un-natural edges in a mold growth pattern look at the end of this cut end of a rafter. If attic conditions were producing mold growth, it would not have stopped so cleanly at the cut surface.

These clues are compelling evidence that this particular mold was on the lumber at the time of construction.


More in-depth review of what mold looks like and stuff that is not mold can be read at http://www.inspect-ny.com/sickhouse/mold.htm#notmold


What to do about mold in buildings

When is mold a problem in buildings? What should be done about it? Find expert field and lab testing, inspection, remediation advice, but ... avoid "fear of mold" and bogus advice which can both cost you and yet may not really address the problem effectively. My interest is in providing expert service to my clients, protecting not only their health but their wallets. I provide field investigations to find problems and to recommend solutions to mold in buildings, and I operate a forensic laboratory in New York which accepts mold and other indoor air and particle samples for examination. In depth information is at www.inspect-ny.com and the links at that page. Website content suggestions are most welcome.

Case Histories: Here I post summaries of field and lab toxic or allergenic mold and other indoor air quality investigations. I omit private information. I describe observations, procedures, and findings helpful to readers who are trying to remedy their own mold, allergenic, carbon monoxide, odor, or other indoor air and related health concerns in their indoor environment.


Daniel Friedman -www.inspect-ny.com